120 ohms is OK, even with a 100mA RCD. IIRC the requirement for an ESS is <200 ohms for "stability", and voltage rise <50V at the trip current which with 100mA would be 12V. Why would it need to be better than that for the genny?Andy wrote: ↑Wed Nov 01, 2023 8:24 pm Cheers sharpener .It is something I have thought of. The house is on 3m deep soil with granite below. It isn't terribly conductive especially when dry. We had 3x2m copper stakes put in for the Quattro but only achieved about 120 Ω. I was wondering if those discs with conductive concrete might be a way to go.
If you can override it for the genny input that will solve your earth bonding problem surely?Andy wrote: ↑Wed Nov 01, 2023 8:24 pmThe gen is on AC1 as that is the logic used in the system operation. If either AC input is live then the default behaviour is top open the ground relay. The assumption is that a neutral to earth connection is provided elsewhere. So in normal operations if I lose the grid then the neutral earth connection is made in the unit. However one is still required if I connect the generator. There is a way to override this behavioursharpener wrote: ↑Wed Nov 01, 2023 3:12 pm Presumably you are connecting the genny to the ACIn 2 as that is what the distinguishes the Quattro from the Multiplus. As I only have the latter I don't know what happens with your internal N-E link relay when the grid fails but the genny input is active. Or whether the ACOut 2 is enabled in this scenario but I think it can be using Assistants. My thinking upthread was that if ACOut 2 is connected to the coil of a n/c contactor this could make an external N-E link whenever it switches off.
Andy wrote: ↑Wed Nov 01, 2023 8:24 pmThis post on the Victron community has the followingAnother downside with generators operating at the AC-input is, that the network type plays an important role. Most smaller gensets are isolated IT type gensets. It is not legally allowed to use them at a house installation by most local laws. You have to use a genset equipped with RCD, those are not the entry level price ones.
Further down Markus then mentions that the easiest solution is just to add a DC charger and then all issues go away. I am still tempted to do this as I am not intending to have the generator sit there waiting for a load. It's incredibly inefficient doing that.
I am not sure what territory Markus is talking about here, some of that discussion centres on Italy which sems to be quite restrictive. For the UK I think there is a permissible earthing scheme in the IEE link you provided and at a practical level I think bonding the genny frame to your earth rod and making sure there is always a neutral link somewhere that does not bypass any of the earth leakage protection is as good as you need.
Most of what Markus says is about getting the Quattro to accept the AC quality of the genny output, and I was surprised to read some of the limitations given that the Quattro is aimed at the market for dual grid/genny supply. So maybe using it to supply the DC side is the best solution after all. He must have money to burn if he is using a Multiplus just for that.
What did the electrician do about providing an earth connection for the genny, and does it comply with the IEE paper?Andy wrote: ↑Wed Nov 01, 2023 8:24 pm I had a house changeover in the past done by an electrician and never got told about which type of generator I could use. Presumably as the victron disconnects from the grid it is ok to use? If the N-E is combined then all the RCDs are downstream of that connection so should presumably function.