I'm really impressed with the one I have installed but we have had a run of miserable days PV wise so had to turn it off for the moment.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
AGT
Posts: 1267
Joined: Sat Jan 29, 2022 11:26 am

Re: More Renewable Shenanigans at Nowty Towers

#202

Post by AGT »

Hi Nowty,

I’m slowly talking SWMBO into the A/C route, can I ask on the Panasonic unit do you wire the mains to the external AC isolator and then a mains/comms cable with the pipework back to the internal unit.
Cheers!
User avatar
nowty
Posts: 6523
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: More Renewable Shenanigans at Nowty Towers

#203

Post by nowty »

AGT wrote: Wed Nov 23, 2022 9:09 pm Hi Nowty,

I’m slowly talking SWMBO into the A/C route, can I ask on the Panasonic unit do you wire the mains to the external AC isolator and then a mains/comms cable with the pipework back to the internal unit.
Cheers!
My unit has an alleged Panasonic compressor, but it is certainly NOT a Panasonic unit. On mine, the mains supply HAS to be supplied to the indoor unit first, then there is a mains interconnector to supply the power through the cable / pipe bundle to the outdoor unit.

There is an internal relay isolator in the indoor unit so if you try and connect the mains power to the outdoor unit and expect the power to flow up the interconnector cable to the indoor unit it won't.

But read the manual because other models may be different.
Last edited by nowty on Thu Nov 24, 2022 9:17 am, edited 1 time in total.
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: More Renewable Shenanigans at Nowty Towers

#204

Post by Oldgreybeard »

nowty wrote: Wed Nov 23, 2022 9:50 pm My unit has an alleged Panasonic compressor, but it is certainly NOT a Panasonic unit. On mine, the mains supply HAS to be supplied to the indoor unit first, then there is a mains interconnector to supply the power through the cable / pipe bundle to the outdoor unit.

There is a relay isolator in the indoor unit so if you try and connect the mains power to the outdoor unit and expect the power to flow up the interconnector cable to the indoor unit it won't.

But read the manual because other models may be different.
Exactly the same for ours. The indoor unit has a normal three core mains cable, then there's a four core power and control cable from there out to the outdoor unit.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
User avatar
Fintray
Posts: 1871
Joined: Mon May 31, 2021 6:37 pm
Location: Aberdeenshire

Re: More Renewable Shenanigans at Nowty Towers

#205

Post by Fintray »

nowty wrote: Wed Nov 23, 2022 9:50 pm
AGT wrote: Wed Nov 23, 2022 9:09 pm Hi Nowty,

I’m slowly talking SWMBO into the A/C route, can I ask on the Panasonic unit do you wire the mains to the external AC isolator and then a mains/comms cable with the pipework back to the internal unit.
Cheers!
My unit has an alleged Panasonic compressor, but it is certainly NOT a Panasonic unit. On mine, the mains supply HAS to be supplied to the indoor unit first, then there is a mains interconnector to supply the power through the cable / pipe bundle to the outdoor unit.

There is a relay isolator in the indoor unit so if you try and connect the mains power to the outdoor unit and expect the power to flow up the interconnector cable to the indoor unit it won't.

But read the manual because other models may be different.
I think I bought the same unit as Nowty (except it is white) but mine has the mains to the outdoor unit.
3.87kWp PV
10.24kWp PV SolarEdge system
Tesla Powerwall 2
MK2 PV router DHW diverter
Morso 5kW WBS
Vaillant AroTherm 10kW ASHP
Nissan Leaf
User avatar
Stinsy
Posts: 3795
Joined: Wed Jun 02, 2021 1:09 pm

Re: More Renewable Shenanigans at Nowty Towers

#206

Post by Stinsy »

AGT wrote: Wed Nov 23, 2022 9:09 pm Hi Nowty,

I’m slowly talking SWMBO into the A/C route, can I ask on the Panasonic unit do you wire the mains to the external AC isolator and then a mains/comms cable with the pipework back to the internal unit.
Cheers!
The European way is to have the mains wired to the indoor unit (followed by a mains/signal 4-core to the outdoor), the American way is to have the mains wired to the outdoor unit (followed by a mains/signal 4-core to the indoor). My unit came pre-wired ready for European-style installation but you can wire it the other way around if you like.

You have to provide means of isolation for anyone servicing the outdoor unit. In a commercial/industrial setting this will be a rotary isolator next to the outdoor unit. However in a domestic dwelling it is also reasonable to isolate at the CU or next to the indoor unit. There is no need to send power back and forth, even if you supply power to the indoor unit first and put a rotary isolator next to the outdoor unit you’re isolating LN and Signal to the outdoor unit.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: More Renewable Shenanigans at Nowty Towers

#207

Post by Oldgreybeard »

I just fitted a 13A fused DP switch next to the indoor unit, spurred off the ring (happened to be a double gang socket right below where I fitted the indoor unit). Makes it easy to isolate the power to work on it, could even pull the fuse out as an extra safety measure. These things need a fused supply anyway, so this seemed the easiest way to do it.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter
User avatar
nowty
Posts: 6523
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: More Renewable Shenanigans at Nowty Towers

#208

Post by nowty »

Stinsy wrote: Thu Nov 24, 2022 6:42 am The European way is to have the mains wired to the indoor unit (followed by a mains/signal 4-core to the outdoor), the American way is to have the mains wired to the outdoor unit (followed by a mains/signal 4-core to the indoor). My unit came pre-wired ready for European-style installation but you can wire it the other way around if you like.
Careful with that as that's what I tried with my second install as the power was nearer the outdoor unit, but the indoor unit would not power up as there is an isolation relay inside the indoor unit. I had to extend pre wired mains lead from the indoor unit down to an area close to the outdoor unit where the power was. So the power ran up the extended mains cable up to the indoor unit, then the power flowed through the 4 core cable back down to the outdoor unit.

EDIT - I guess you could parallel up the mains cables in the indoor unit, but that would defeat the purpose of the isolation relay inside the indoor unit.
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
User avatar
Stinsy
Posts: 3795
Joined: Wed Jun 02, 2021 1:09 pm

Re: More Renewable Shenanigans at Nowty Towers

#209

Post by Stinsy »

Oldgreybeard wrote: Thu Nov 24, 2022 8:49 am I just fitted a 13A fused DP switch next to the indoor unit, spurred off the ring (happened to be a double gang socket right below where I fitted the indoor unit). Makes it easy to isolate the power to work on it, could even pull the fuse out as an extra safety measure. These things need a fused supply anyway, so this seemed the easiest way to do it.
And that is perfectly acceptable in a domestic setting. Imagine a shop/office/factory, the guy working on the outside unit needs to be able to isolate it within eyesight so that he can be confident no one will re-energise it without his knowledge.

If someone wants to fit a rotary isolator next to the external unit at their house, they can. But it isn't "required".
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
Oldgreybeard
Posts: 1873
Joined: Thu Sep 09, 2021 3:42 pm
Location: North East Dorset

Re: More Renewable Shenanigans at Nowty Towers

#210

Post by Oldgreybeard »

Stinsy wrote: Thu Nov 24, 2022 10:33 am
Oldgreybeard wrote: Thu Nov 24, 2022 8:49 am I just fitted a 13A fused DP switch next to the indoor unit, spurred off the ring (happened to be a double gang socket right below where I fitted the indoor unit). Makes it easy to isolate the power to work on it, could even pull the fuse out as an extra safety measure. These things need a fused supply anyway, so this seemed the easiest way to do it.
And that is perfectly acceptable in a domestic setting. Imagine a shop/office/factory, the guy working on the outside unit needs to be able to isolate it within eyesight so that he can be confident no one will re-energise it without his knowledge.

If someone wants to fit a rotary isolator next to the external unit at their house, they can. But it isn't "required".
I've locked off supplies many times over the years. Almost all of those lock offs will have been with a bog standard lockable clamp, with a small padlock fitted to it and a warning tag with my name on it. I can count on one hand the number of times I've locked off a rotary isolator, TBH. I've also locked off standard 13A switch fuses a few times, just pull the fuse and stick a cable tie and warning flag through the empty fuse holder. My bag of goodies includes half a dozen standard lock-off clamps that will fit any circuit breaker or RCD etc with a manual operation lever. I would be very surprised if any electrician didn't also have lock-off clamps and understand how to use them for safe isolation, TBH. There has never, ever, been any requirement in the regs for an isolator to be within eyesight at the point of work.