nowty wrote: ↑Mon Sep 12, 2022 11:30 pm
Kenny000666 wrote: ↑Mon Sep 12, 2022 10:28 pm
Just reread the declaration. Sounds like it can be signed by the Generator I.e me. So maybe I can just use any spark to wire it up as long as they don’t need to get involved with the G99 commissioning form.
Thats exactly what several on here have done.
On this note, is anyone on here able to help fill out the commissioning forms?
Particularly:
- What did everyone put down for the installer? Is it ok to just put TBC, or N/A, or my details? It asks for a signature of installer, so im hesitant to put this in front of the electrician.
- for the question: "Interlocking that prevents PGMs being connected in parallel with the DNO’s Distribution Network (without synchronising) is in place and operates correctly." - does this mean that if the grid goes down the device also turns off? If so i think the Solis RAI needs this
- for question: "As installed Standard Application Form data, unless already provided." what is standard application form data?
- for the part that says - "*delete if not applicable ie if the Interface Protection and ride through capabilities are Type Tested" - i assume that because the SOLIS RAI 5G is registered on as a Fully Type Tested device on the ENA site, with G98, G99 and G100 certs, this is true and i can delete these parts?