BMS communication issues

cojmh
Posts: 294
Joined: Wed Mar 16, 2022 8:11 pm
Location: West Midlands

Re: BMS communication issues

#31

Post by cojmh »

I completely agree .... assume nothing and test everything!

A bit of an update.

I decided to leave the batteries online (I normally turn them of as I don't like the idea of them being on if I don't know they are working properly)

It would seem they are now willing to discharge - the only problem is that the inverter is discharging them to the grid (which is the opposite of what I want to see!)

So I have now seen that the batteries will discharge, but not correctly (and at the maximum discharge rate which seems to have reset itself to 50A)

I will have to see if I can get hold of the manufacturers.
User avatar
nowty
Posts: 6534
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: BMS communication issues

#32

Post by nowty »

The calibration (i.e the direction) f your grid CT clamp may be wrong.
19.6kW PV > 117MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
cojmh
Posts: 294
Joined: Wed Mar 16, 2022 8:11 pm
Location: West Midlands

Re: BMS communication issues

#33

Post by cojmh »

I didn't realise there was a direction.

It is very possible - just before I installed the batteries, I had a new smart metre installed by British Gas which included a an isolator switch - so I know they had to disconnect the grid clamp and they might have put it back wrong.

I will have a look at that .... is there any directional markings on the clamp?

Thanks,
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: BMS communication issues

#34

Post by Joeboy »

There should be.
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: BMS communication issues

#35

Post by Joeboy »

Can you post a photo?
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
cojmh
Posts: 294
Joined: Wed Mar 16, 2022 8:11 pm
Location: West Midlands

Re: BMS communication issues

#36

Post by cojmh »

OK,

I have just had a look and referenced the Solax documentation and it is indeed pointing in the wrong direction. There is an arrow on it that is supposed to point to the public grid .... mine points to the consumer units.

Before I start fiddling with the CT sensor do I need to turn off the power or turn off the inverter?

Or can I simply unclip the CT sensor and clip it back on the correct way around without doing anything to the inverter?

Thanks - I would never have thought to look at that!
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: BMS communication issues

#37

Post by Joeboy »

Here's mine, the black one.
Image

Image
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: BMS communication issues

#38

Post by Joeboy »

cojmh wrote: Sat Apr 02, 2022 4:06 pm OK,

I have just had a look and referenced the Solax documentation and it is indeed pointing in the wrong direction. There is an arrow on it that is supposed to point to the public grid .... mine points to the consumer units.

Before I start fiddling with the CT sensor do I need to turn off the power or turn off the inverter?

Or can I simply unclip the CT sensor and clip it back on the correct way around without doing anything to the inverter?

Thanks - I would never have thought to look at that!
Unclip.
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
User avatar
Joeboy
Posts: 9415
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: BMS communication issues

#39

Post by Joeboy »

I sincerely hope it has been a CT clamp and wrongly wired bms lead. Fingers x'd.
17.55kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
Tinbum
Posts: 1285
Joined: Mon May 31, 2021 9:55 pm

Re: BMS communication issues

#40

Post by Tinbum »

Your cable certainly seems ok at the battery end and from what you have said the inverter end looks ok.

I would drop the Voltage down to 53.2v as that is the max the battery will every request. Their are many warnings not to over volt the batteries as it can easily lead to a new bms being needed.

I think you are going to have to go back to Solis and ask them to confirm the pinouts and that their protocol is ok for the USx000C and if not they need to bring a new firmware out.

Have you tried using a different one of your batteries as the master, just to rule out a battery fault?
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
Post Reply