Armoured cable for DC

AGT
Posts: 1267
Joined: Sat Jan 29, 2022 11:26 am

Re: Armoured cable for DC

#21

Post by AGT »

Thought inverters did insulation resistance tests before energising?
Also wonder if fuses in the string would help mitigate the risk?
Tinbum
Posts: 1285
Joined: Mon May 31, 2021 9:55 pm

Re: Armoured cable for DC

#22

Post by Tinbum »

AGT wrote: Sun Oct 27, 2024 10:44 am Thought inverters did insulation resistance tests before energising?
Also wonder if fuses in the string would help mitigate the risk?
You'd need the fuses at the pv end.
85no 58mm solar thermal tubes, 28.5Kw PV, 3x Sunny Island 5048, 135kWh Rolls batteries, 52kWh Growatt storage GBLI 6532, 66kWh Pylontech US3000C, 43kWh DIY, Sofar ME3000's, Brosley wood burner and 250lt DHW
AGT
Posts: 1267
Joined: Sat Jan 29, 2022 11:26 am

Re: Armoured cable for DC

#23

Post by AGT »

Yes i know, some kind of PV combiner box/ fuse set up , but I suppose access becomes a challenge for these things….

https://www.windandsun.co.uk/collection ... g8QIqNsKJq
wookey
Posts: 57
Joined: Mon Oct 18, 2021 4:44 am

Re: Armoured cable for DC

#24

Post by wookey »

You aren't allowed to put DC down T&E either 'because it's not double-insulated'. i.e it's insulated and sheathed which isn't the same thing. I don't actually know the spec but I'd be surprised if it couldn't take 600VDC quite happily.
I suppose the point is that exposed DC is a lot more dangerous than exposed AC so they are being very paranoid, which isn't completely crazy for T&E, but it does seem pretty silly for SWA.
DIY deep 1960's house retrofit: http://wookware.org/house/retrofit
MVHR, airtightness, IWI, EWI, 3G windows, 7kW PV, 16kWh battery, woodburner,
perimeter insulation, extension, garage conversion, UFH, 1200l water butts, garden veg
User avatar
Stinsy
Posts: 3793
Joined: Wed Jun 02, 2021 1:09 pm

Re: Armoured cable for DC

#25

Post by Stinsy »



Here you go. The IET has finally ruled that SWA isn’t allowed for the DC side of solar installations.
12x 340W JA Solar panels (4.08kWp)
3x 380W JA Solar panels (1.14kWp)
6x 2.4kWh Pylontech batteries (14.4kWh)
LuxPower inverter/charger

(Artist formally known as ******, well it should be obvious enough to those for whom such things are important.)
robl
Posts: 77
Joined: Fri Apr 01, 2022 8:41 pm

Re: Armoured cable for DC

#26

Post by robl »

There’s no point fusing the cable at the panel end - the mppt will run them at 90% or so of their short circuit current. You’ll not find a fuse that will work normally, then blow when you want.
4kWp solar, EV

MVHR, 150mm EWI, 15kWh batt, 2.5kW GSHP, no gas, 7.5kW PV, TM3 + leaf ‘cos can’t insure kids for TM3