Adokforme wrote: ↑Sat Sep 25, 2021 2:23 pm
How powerful is the heating element?
Thanks for prompt and positive reply Stinsy. 3 kW, two off. Thermal store is 210 litre. Thanks too for mentioning radial. I'm running two 2.5mm2 cables into a double socket so I guess ring main was an elaborate description.
How many elements (immersion heater?) of what power will be used for the thermals store? Will you be using a PV diverter?
Thanks Countrypaul, No diverter, although it is tempting. But with a 40 kWh, battery on wheels in the drive, I'm hoping one day to link it up via V2H/G which might then make the diverter somewhat superfluous! We've an almost 9 kW array on the roof and in fine weather generating 6 kW. Ample to power just the one element which is all we do. But there has been the odd occasion when a shorter heating period would have been convenient. Hence for putting them on their own circuit so not overloading existing supply.
Thanks too for the tip re Notifiable.
Thanks for the additional information.
- A radial run in 2x lengths of 2.5 is non-conventional, that isn't to say it is prohibited but it could present challenges in future (eg if you needed an EICR for any reason).
- Most double sockets are only rated for 13A combined. Connecting 2x 13A loads would overload it. In any case connecting an immersion via a plug/socket isn't recommended. Use a FCU instead.
- For your situation here is what I would suggest: 1) If both immersions can be used simultaneously run a 32A radial in 4mm. 2) If only one immersion is likely to be used (EG you're using an E7 controller / solar diverter) then either a 16A radial in 1.5mm or 20A in 2.5 will be sufficient.
- Incidentally with 9kWp on the roof it is borderline criminal not to have a diverter! You're throwing electricity away! A Zappi (or similar) EV charging point can do the same for your EV. It'll only go one way, but it is available now.