Voltage delta?
Hi,
My newest Chinese stack is ready, 15 x 230Ah cells & sitting at an overall, cell balanced, voltage of 49 volts.
Question is, if I want to bring them into service in parallel with another stack, what’s the maximum voltage difference I should consider making the connection at? I’m assuming that ANY difference will cause a momentary stress to each bank? I could link with a low value resistance & let things equalise a while and them remove when there is zero difference?
Comments welcome.
Thanks- Rob
My newest Chinese stack is ready, 15 x 230Ah cells & sitting at an overall, cell balanced, voltage of 49 volts.
Question is, if I want to bring them into service in parallel with another stack, what’s the maximum voltage difference I should consider making the connection at? I’m assuming that ANY difference will cause a momentary stress to each bank? I could link with a low value resistance & let things equalise a while and them remove when there is zero difference?
Comments welcome.
Thanks- Rob
Re: Voltage delta?
Just looking back when I added a 48V parallel string. I first tried at 3V difference and that was over 100A, maybe a lot over so I re-tried at 0.75V difference using a fuse to make the connection just in case. That was a more comfortable 50A or so.
I would say 1V or under (full stack voltage) would be ok.
Its always scary though.

I would say 1V or under (full stack voltage) would be ok.

Its always scary though.


18.7kW PV > 111MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
-
- Posts: 662
- Joined: Mon Mar 21, 2022 7:37 pm
Re: Voltage delta?
Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?
Morso S11
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery
Re: Voltage delta?
Can you avoid the playing with plasma by just charging both packs fully before connecting?
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, 50kWh Akvaterm Thermal Store (750l)
Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
Re: Voltage delta?
I don't think it really matters much. The high current (which will be limited by the cable/connector resistance) will only last a very short time.
Andy from the off grid garage has done a video on this.
If your really worried use a 0.1 ohm resistor which will keep the current below 100A even if there's a 10V difference.
I didn't bother when I paralleled my 4 banks, but they were charged to fairly close voltages.
Andy from the off grid garage has done a video on this.
If your really worried use a 0.1 ohm resistor which will keep the current below 100A even if there's a 10V difference.
I didn't bother when I paralleled my 4 banks, but they were charged to fairly close voltages.
Re: Voltage delta?
I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.
Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.
No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.
No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
-
- Posts: 236
- Joined: Fri Mar 11, 2022 7:48 pm
- Location: Lincolnshire
Re: Voltage delta?
I did make that comment in my OPopenspaceman wrote: ↑Mon Jan 22, 2024 7:25 pm Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?
-
- Posts: 236
- Joined: Fri Mar 11, 2022 7:48 pm
- Location: Lincolnshire
Re: Voltage delta?
I think that’s the way I’ll do it tomorrow. A combination of my “low resistance” and using the electric oven to drawdown ……..Joeboy wrote: ↑Mon Jan 22, 2024 9:21 pm I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.
Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.
No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
Re: Voltage delta?
Remember to give the homestack time to settle to an accurate reading once you remove the oven load. A minute or two should do it.Lincs Robert wrote: ↑Mon Jan 22, 2024 9:36 pmI think that’s the way I’ll do it tomorrow. A combination of my “low resistance” and using the electric oven to drawdown ……..Joeboy wrote: ↑Mon Jan 22, 2024 9:21 pm I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.
Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.
No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?![]()

Congratulations BTW!
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
-
- Posts: 662
- Joined: Mon Mar 21, 2022 7:37 pm
Re: Voltage delta?
Yes but I was thinking a higher resistance for a longer time and asking more than suggesting.Lincs Robert wrote: ↑Mon Jan 22, 2024 9:33 pmI did make that comment in my OPopenspaceman wrote: ↑Mon Jan 22, 2024 7:25 pm Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?![]()
Morso S11
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery
FIT
4kW panels facing WSW
Solarmax 4200S
Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE
2.6kW facing WSW
Sunsynk 3.6kW inverter
Storage
10.4kWh GLS lithium phosphate battery