My newest Chinese stack is ready, 15 x 230Ah cells & sitting at an overall, cell balanced, voltage of 49 volts.

Question is, if I want to bring them into service in parallel with another stack, what’s the maximum voltage difference I should consider making the connection at? I’m assuming that ANY difference will cause a momentary stress to each bank? I could link with a low value resistance & let things equalise a while and them remove when there is zero difference?

Comments welcome.

Thanks- Rob
User avatar
nowty
Posts: 6400
Joined: Mon May 31, 2021 2:36 pm
Location: South Coast

Re: Voltage delta?

#2

Post by nowty »

Just looking back when I added a 48V parallel string. I first tried at 3V difference and that was over 100A, maybe a lot over so I re-tried at 0.75V difference using a fuse to make the connection just in case. That was a more comfortable 50A or so.

I would say 1V or under (full stack voltage) would be ok. :xx:

Its always scary though. :?

Image
18.7kW PV > 111MWh generated
Ripple 6.6kW Wind + 4.5kW PV > 34MWh generated
7 Other RE Coop's
105kWh EV storage
90kWh Home battery storage
40kWh Thermal storage
GSHP + A2A HP's
Rain water use > 530 m3
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Voltage delta?

#3

Post by openspaceman »

Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?
Morso S11
FIT
4kW panels facing WSW
Solarmax 4200S

Non FIT
disparate string
1.75kW facing SSE
0.85kW facing NE

2.6kW facing WSW

Sunsynk 3.6kW inverter

Storage
10.4kWh GLS lithium phosphate battery
User avatar
AlBargey
Posts: 201
Joined: Mon Oct 11, 2021 8:41 pm

Re: Voltage delta?

#4

Post by AlBargey »

Can you avoid the playing with plasma by just charging both packs fully before connecting?
38m Barge, Solar (10.6 kWp), 26 kWh of LFP, 50kWh Akvaterm Thermal Store (750l)
Victron Quattro 8 kVA, CerboGX, 3,500L STP, 57kVa Perkins
Our live data: https://vrm.victronenergy.com/installat ... e/c76c4bf6
HML
Posts: 44
Joined: Sun Sep 03, 2023 1:56 pm

Re: Voltage delta?

#5

Post by HML »

I don't think it really matters much. The high current (which will be limited by the cable/connector resistance) will only last a very short time.

Andy from the off grid garage has done a video on this.

If your really worried use a 0.1 ohm resistor which will keep the current below 100A even if there's a 10V difference.

I didn't bother when I paralleled my 4 banks, but they were charged to fairly close voltages.
User avatar
Joeboy
Posts: 9100
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Voltage delta?

#6

Post by Joeboy »

I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.

Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.

No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
Lincs Robert
Posts: 236
Joined: Fri Mar 11, 2022 7:48 pm
Location: Lincolnshire

Re: Voltage delta?

#7

Post by Lincs Robert »

openspaceman wrote: Mon Jan 22, 2024 7:25 pm Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?
I did make that comment in my OP 👍
Lincs Robert
Posts: 236
Joined: Fri Mar 11, 2022 7:48 pm
Location: Lincolnshire

Re: Voltage delta?

#8

Post by Lincs Robert »

Joeboy wrote: Mon Jan 22, 2024 9:21 pm I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.

Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.

No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
I think that’s the way I’ll do it tomorrow. A combination of my “low resistance” and using the electric oven to drawdown …….. 🤞
User avatar
Joeboy
Posts: 9100
Joined: Mon May 31, 2021 4:22 pm
Location: Inverurie

Re: Voltage delta?

#9

Post by Joeboy »

Lincs Robert wrote: Mon Jan 22, 2024 9:36 pm
Joeboy wrote: Mon Jan 22, 2024 9:21 pm I seem to remember I charged my new pack so far (say 70%) then did a drawdown on the existing home pack to match as close as possible.

Even being a measured couple of hundredths of a Volt between them I still got a nice fat spark on final connection.

No harm done as far as I could see. I guess with hindsight I'd try and match packs at the lower end of the scale but that'll be kind of dictated by the soc of the new to be connected pack once its balanced?
I think that’s the way I’ll do it tomorrow. A combination of my “low resistance” and using the electric oven to drawdown …….. 🤞
Remember to give the homestack time to settle to an accurate reading once you remove the oven load. A minute or two should do it. :xl:

Congratulations BTW!
15kW PV SE, VI, HM, EN
42kWh LFPO4 storage
73kWh V2H EV
7kW ASHP
200ltr HWT.
3G
Deep insulation, air leak ct'd home
WBSx2
Low energy bulbs
Veg patches & fruit
openspaceman
Posts: 662
Joined: Mon Mar 21, 2022 7:37 pm

Re: Voltage delta?

#10

Post by openspaceman »

Lincs Robert wrote: Mon Jan 22, 2024 9:33 pm
openspaceman wrote: Mon Jan 22, 2024 7:25 pm Wouldn't it be a little less exciting to wire a big resister (like the element from an electric fire) between them, let them equalise and then join the busbars?
I did make that comment in my OP 👍
Yes but I was thinking a higher resistance for a longer time and asking more than suggesting.