First 'real' post so take it easy on me

Looking at the manual, most of it make sense apart from one bit (though annoyingly the pdf is read only

Thanks!
Thanks, yes that was the section that I was referring to that then just abruptly ends - question was where the other two ends go for the logic trigger switch?Moxi wrote: ↑Thu Aug 25, 2022 10:36 am Ahh sorry Umski,
I'm trying to copy paste the section from the manual but not getting anywhere.
Section 4 located at Page 15 (top) indicates the Demand Response Monitor is made up from an RJ45 utilising pins 5 and 6, a length of coms cable and a switch.
With the switch open circuit the Inverter operates normally, switch closed, the inverter shuts down within 5 seconds.
No idea why the cable and switch isn't included in the box for the UK market but is a quick and easy build.
Moxi
Thanks, that was what I was thinking too - it's just the manual kind of implies that somehow the DRM control is needed for the UK - it seems kind of vague however!marshman wrote: ↑Thu Aug 25, 2022 10:36 am On my Solis Hybrid inverter the Acrel meter plugs into its own RS485 connector on the inverter. The DRM (Demand Response Management) is a separate and unused connector - well I'm not using it! As far as I can tell it is so the inverter can be remotely shut down or started up for some reason other than grid controlled parameters.