ChrisJEvans wrote: ↑Sat Nov 26, 2022 4:28 pm
I am getting a qualified electrician to do the AC side of my PV. I'm sourcing all the components and want to check what I'll need.
I don't think I need a Henley block to wire in the inverter as I have spare circuits on my consumer unit.
Is that correct?
A Henley block is the wrong type of connector for something as low power as this, as they are usually for fatter cables (meter tails typically). No need for any interconnection, it's fine to connect the cable from the AC isolator directly to the RCBO or MCB in the consumer unit (it does need to have RCD protection, so either on an RCBO or an MCB protected by an RCD)
ChrisJEvans wrote: ↑Sat Nov 26, 2022 4:28 pmDo I need a separate breaker between the inverter and the consumer unit?
Yes, normally this would be an AC DP isolator, often fitted adjacent to the inverter.
ChrisJEvans wrote: ↑Sat Nov 26, 2022 4:28 pmFor the Backup AC output of the Inverter do I need an isolator in the loft next to the circuit breaker?
Depends how the inverter does the AC backup. Some have an internal changeover relay, so the same AC output serves both purposes and there is no need for any further isolation. Some have two AC connections, a normal grid power one and a second backup power one. If you have one of the latter then both need isolators, not just the grid one.
ChrisJEvans wrote: ↑Sat Nov 26, 2022 4:28 pmI will have a SP3T change over switch next to the consumer unit so that the critical load consumer unit can be switched if say the Inverter had to be removed.
(Goodwe inverters instructions say this is a requirement though I'm hoping to collect a Solis inverter on Monday and Solis don't mention one)
The topic of grid and backup switching and isolation can get complex, as unless your installation has TT earthing then you need to be able to provide a TT earth in backup mode, as the chances are the supplier's incoming earth will not be present in a power cut. You may also need to arrange for the earth and neutral to be linked in backup mode, as not all inverters do this. In theory you can run the back up supply as IT, with neither AC conductor connected to earth, but it's likely that most electricians won't have come across an IT supply and may not feel happy signing such an arrangement off.
My solution was simplified as our installation already had TT earthing, so all I needed to do was make sure that the neutral and earth are linked when the inverter is in backup mode. I have a feeling that there may be some info on whether the Solis connects neutral to earth in backup mode in another thread here, might be worth a look around to find posts about this.
ChrisJEvans wrote: ↑Sat Nov 26, 2022 4:28 pmThe inverter installation manual talks of using round AC cables. It will be in the loft so IP rating is not a concern, can I use standard flat twin and Earth?
T&E is fine in the loft, no need for any greater protection. Only slight issue may be the cable glands on the inverter. Ours came with oddball glands that accepted three separate conductors, which would be against the regs to use here, so I swapped them for round cable glands and used 2.5mm² flex to connect to a junction box. If you need round rigid cable to fit the inverter glands then NYY-J cable would be fine, or you could just use a short length of flex to connect to the AC isolator and T&E from there.
25 off 250W Perlight solar panels, installed 2014, with a 6kW PowerOne inverter, about 6,000kWh/year generated
6 off Pylontech US3000C batteries, with a Sofar ME3000SP inverter